Hi
I have Multi plus 24/3000 no ess installed ,is the follow possible if so how can it be done
Is is possible for the multi to ignore the ac input and just use the battery until large loads is turned on.
Example would be a load of 600w comes from battery no ac input but if a load of 1800w is used then it’s taken from the grid with battery’s
When 1800w load has gone ac is ignored again and power supplied from battery
Thanks