Isolation transformer 120/240 US to 230v Euro

I’m trying to find out if the 7,000 watt 230v to 230v isolation transformer will take 120v/240v split phase (120v to ground, 240v leg to leg) and output 230v to ground. We have a European powered boat that is wired for 230v to ground and the breakers for the 230v panel are only single breakers, as the neutrals are to a common buss. We want to use incoming US power but not be concerned that we have not protected the wires on both legs. Our equipment does run fine on either 50hz or 60hz.

Isolation Tranformer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

If the transformer is a proper isolating transformer then test the 230V output IS isolated from ground before connecting. If this is so, then having single pole breakers on the 230V side is no issue. However, if the transformer casing is metallic and connected to shore ground, it should be isolated from any fitting inside the yacht, and covered from touch - as it will be at shore ground potential. Do make sure that the shore supply is protected by an RCCD.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

teetera avatar image teetera commented ·

I don’t have the Victron isolation transformer yet. We have a no name IT now.

My question is more about the input vs output of the Victron IT. If it outputs the 240v to ground even if 120/240 is input. The IT we have now does not, it outputs whatever is input.

0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The datasheet says the 7000VA transformer is only to transform 230V to 230V.

https://www.victronenergy.com/upload/documents/Datasheet-Isolation-Transformers-EN.pdf

The other models can also transform 120V to 230V.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rod avatar image
Rod answered ·
So Victron doesn’t offer “Split-phase isolation transformers” to use in combination with Victron Multiplus-II 2 x 120V split-phase 120/240V 3000 VA 60 Hz
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.