teekay asked

2 alternators and 2 Orion-Tr Smart 12/12-18A Lead Acid bank

Hi, thanks for looking at this. I have a boat with 2 x 6 cylinder diesel engines. I believe the alternators are around 40A each. I have a bank of 2 110Ah lead acid batteries. I'm thinking of getting 2 Orion-Tr Smart isolated 12/12-18A units, one for each engine and then have the outputs both going to the battery bank in parallel. Will they work okay together like this or is there anything else I need to consider? Cheers.

orion-tr smartalternator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

The two Orion's should work ok in parallel, as long as they both have the same configuration. You might want to look at a higher current rating for faster charging though.