question

bluesky027 avatar image
bluesky027 asked

Smart mppt 75/15 not charging

7a1d8ccd-31f0-4022-b256-ac2a166ffac2.pngI have 3 solar panel 200 watts each with 3 mppt 75/15 all have the fuse at the connection under the solar panel, the wire from solar panel all meet in a busbar and from there go directly to the battery. The solar panel will charge the batter for 1-2 days and after will stop, i need to unplug both terminal from solar panel negative and positive at the battery . Once I unplug and plug back again will start to work, When is not working I have power coming from solar panel is just the battery not accepting it. I have lithium battleborn lifepoo4 with Bms battery a Victron multiplus 3000 and the color control panel and a smart shunt. 2b571c4f-33a8-45db-b79d-5286a095d8d7.png44600199-8490-4e01-8224-7e2dc53a4803.png

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Bluesky027

From what I can see your Vmax on your solar panels is barely above 5v of the battery voltage. so most of the time the charger will not start.

https://www.youtube.com/watch?v=EVAvRs32TiE

https://www.youtube.com/watch?v=EVAvRs32TiE

You need higher panel voltage (more panels in series). You have also limited the charger 5A output is there a reason for that?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.