question

andrewelliott avatar image
andrewelliott asked

Can I switch on and off a Multiplus inverter using Cerbo GX

Hi


This might be a newbie question, I have my multiplus connected to the Cerbo GX the GX is communicating and reading status. Is it possible to switch the inverter on and off using the cerbo through the Victron Connect APP.


Thanks

cerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
JohnC avatar image
JohnC answered ·

Hi @andrewelliott

Yes you can. You'll need to select Remote Console and find this..

1623241040323.pngSelect the Switch line and a new screen shows with the option to change it to Off.


1623241040323.png (120.2 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

andrewelliott avatar image andrewelliott commented ·

Thanks John much appreciated

0 Likes 0 ·
conradzik avatar image conradzik commented ·

What about when a VE.Bus BMS is present? The switch is disabled if one is connected.

0 Likes 0 ·
bathnm avatar image bathnm conradzik commented ·

Correct

0 Likes 0 ·
Kevin Windrem avatar image
Kevin Windrem answered ·

You can also find the inverter mode on the Mobile Overview page, enabled in the Display and Language setup page. This, too would be disabled with a VE.Bus BMS.

2 |3000