question

donnyv avatar image
donnyv asked

Does mppt ground need to connect directly to smart shunt load

Hi,


I am connecting a MPPT 100 20 and a smart shunt. The mppt is utilized for 2 90W solar panels input.

The wiring diagram I am using shows to connect the mppt battery negative directly to the load connection of the shunt.

Can I instead connect the load side of the shunt to a ground bus bar, and connect mppt negative to that, or does the mppt need to connect to the shunt? Will this affect any readings?

Thanks

MPPT SmartSolarSmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @DonnyV,

it is not uncommon to connect MPPT battery minus to a ground bus bar and have the bus bar connected to the load side of the shunt. It does not affect the reading.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.