System: Multiplus-II, Venus GX, Energymeter ET340, PV-Inverter: 3x Envertech EVT560.
Grid feed back ist allowed, The system is feeding Energy Into the grid, but it is not displayed in the VRM dashboard. What did I do wrong?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
System: Multiplus-II, Venus GX, Energymeter ET340, PV-Inverter: 3x Envertech EVT560.
Grid feed back ist allowed, The system is feeding Energy Into the grid, but it is not displayed in the VRM dashboard. What did I do wrong?
Could you please make some screenshots of your VRM site?
If I understand it correctly it could be the visualization issues with the ET340 in a 3-phase system with only 1-phase ESS.
In such a setup you should use an EM24 instead of the ET340.