Multi 2 supplying loads on the ac input (ESS system)

Is there a way to have loads that are grid connected only but still monitored through the VRM, I tried putting the loads after the external energy meter on the grid side but the multi is still feeding them from the battery.

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
markus avatar image
markus answered ·

Yes. You can use AC-OUT2 output for those loads.

See here: Multiplus2 Manual (victronenergy.de)

BR

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dane avatar image
dane answered ·

markus, i want some of the loads to be fed from the grid directly due to high start up currents outside of the multiplus limits, i would also like to limit any unnecessary drain on the batteries, my understanding is as normally there would be grid available all the time on the AC-IN1 any loads on AC-OUT2 would still be fed from the batteries until the total load is outside the battery discharge limits or if the grid fails.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markus avatar image markus ♦♦ commented ·

Ok, then take a look at the programmable relay assistant.

1622546422741.png

1622546447536.png

1622546490485.png

1622546531444.png

You will have to set up a separate assistant for "on" and another one for "off"

BR