I have been installing Solar on a 5th wheel which consist to 6 x 175 watt panel, into a Victron MPPT 100/50 Charge controller charging. 4x6 interstate GC batteries rated at 420 AH @20. I have set the Charge to Battery Voltage 12
Max Charge Current CC/10 which is 42 Amps
Absorpon Voltage is 15.3V
Float Voltage is 13.4
Equalization Voltage is 15.6 Volts
All settings are from the INTERSTATE BATTERY Recommendations.
For the BMV-712 Setting I'm Using
Battery Capacity 420
Charge Voltage ? ( I'm reading that it should be a few % below the Absorption Voltage say 15V)
Tail Current 4% (Which I'm assuming would be 16.8 Amps)
Charged Detection Time 3m
Peukert exponent 1.25
Charge Efficency Factor 80%
Current Threshold .10A
Time-to-go average period 3m
Does this look right?