Hi!
What register is for getting the charge state of the battery via modbus. I tried 30 but the value is always 0 ...
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi!
What register is for getting the charge state of the battery via modbus. I tried 30 but the value is always 0 ...
Solution: It is Modbus register 266 on unit ID 225
No! That didn't work. Always 0
That's wierd. I am using address 843 to read my Pylontech SOC.
Did you set slave address to 100?
As an example, this is the configuration in my Homeassitsant modbus file:
- name: "Battery Level"
scan_interval: 10
unit_of_measurement: "%"
slave: 100
address: 843
Thank you for your information. Meanwhile I found the solution by myself :-) See my last answer...
28 People are following this question.