Using 2 Quattro 120V/48/3000W in Split mode connected to a CCGX. System also includes MG Energy Lynx BMS, 3xMPPT.
Quattro had no Assistant installed.
System was not conneted to any Grid source. used as Off grid mode only. using a generator to recharge batteries only twice in the last 6 months.
Wanted to upgrade system
Now Quattro connected on
- AC1 to Split phase power from Bahamas power.
- AC2 now connected to a generator input.
- Upgraded Quattro from 463 to 482
- Upgraded CCGX from 2.63 to 2.66
- added VS Ignore Ac Input to both units.
As long as i do not connect the quattro to the CCGX, the Quattro operates. Within 30sec of plugging the CCGX, get Error #10 : System time synchronization problem occurred
Error also happens if the Quattro are set to Charge only.
Lights on the master go away, lights on the Slave show loss of syncronization. Seems like the Master quattro is reseting. 30 seconds or so later error goes away only to reoccur 30 second later.
Try 3 different set of cable. They all work if only connecting the 2 Quattro. Error only occur when you plug the CCGX.
Try 2 different CCGX same
Try to move ports around same
Used contact cleaner on VE. Bus ports
Checked Ground voltage from CCGX 0 volt source (BMS voltage regulated output) to Quattro ground. All good.
Checked for Battery fuse: Good
Checked tight Connection: Good.
Any suggestion would be welcome.