Hello,
Is there any way we can start/stop a generator based on a load appearing on AC out 2 of a Quattro? I can't see this condition in the CCGX, is there a way to use the programmable relay for this using an assistant?
Thanks.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello,
Is there any way we can start/stop a generator based on a load appearing on AC out 2 of a Quattro? I can't see this condition in the CCGX, is there a way to use the programmable relay for this using an assistant?
Thanks.
What about using the ACout 2 relay condition as per below? Does this drive the programmable relay based on a load on AC 2?
No, you can drive the AC out 2 relay with as one of the programmable relays.
What exactly do you want to accomplish? maybe there is a smart solution available.
Usually you drive the generator start / stop based on SOC / battery voltage combined with the total load (AC1 + AC2)
Internally, the inverter only measures total output, and cannot differentiate what's on AC1 and AC2.
They want to be able to turn on the generator when there is a call for hot water which is wired via AC out 2.