Gen start/stop

Hello,

Is there any way we can start/stop a generator based on a load appearing on AC out 2 of a Quattro? I can't see this condition in the CCGX, is there a way to use the programmable relay for this using an assistant?


Thanks.

CCGX Color ControlGenerator
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

AFAIK: No, only the total load on both outputs can be used.

0 Likes 0 ·
1 Answer
stevo07 avatar image
stevo07 answered ·

What about using the ACout 2 relay condition as per below? Does this drive the programmable relay based on a load on AC 2?


1550593431335.png (15.6 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

No, you can drive the AC out 2 relay with as one of the programmable relays.

What exactly do you want to accomplish? maybe there is a smart solution available.

Usually you drive the generator start / stop based on SOC / battery voltage combined with the total load (AC1 + AC2)

Internally, the inverter only measures total output, and cannot differentiate what's on AC1 and AC2.

1 Like 1 ·
stevo07 avatar image stevo07 boekel ♦ commented ·

They want to be able to turn on the generator when there is a call for hot water which is wired via AC out 2.

0 Likes 0 ·
boekel avatar image boekel ♦ stevo07 commented ·

either run a relay along the heater when it switches on, to one of the inputs of the multi, or the simple way: use total AC use to activate the generator. if the heater is 3kW, you can use 3kW as a value.

0 Likes 0 ·