150V controller derate

ts-mppt-60a-derate.jpgI am searching for technical aspect of the MPPT 150V controllers. Specifically at what point the controller starts to derate with regards to heat sink temp and array input voltage. I currently use two Morningstar TS MPPT 60A and they derate the output current when heatsink is over 80 deg C and array input is over 115V... the graphs are in the user manual.

Is there a similar derate graph/ spec for the Victron MPPT 150V controllers?

TIA

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

These units operating input Voltage is up to 145V without derating.

Full output power up 40°C ambient and then an operating maximum of 60°C.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rithym1964 avatar image rithym1964 commented ·

Okay that's good to know my panels are 200W and I have to keep the strings at max 3 panels to keep the VOC below 115V. I tried strings of 4 but the 60A controller wouldn't charge above 45A as the VOC was around 130V. I am going to purchase a victron MPPT 150/85 (similar price) and replace a Tristar and see how the output compares. I imagine the Victron heat sink will go above 40 here in the Summer but I can always add a cooling fan.

-1 Like -1 ·
rithym1964 avatar image rithym1964 rithym1964 commented ·

Also I can change the strings on the Victron to 4 x 6 rather than 3 x 8 currently with the Tristars.

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ rithym1964 commented ·

If a string of 4 of your panels is 130V Voc then that would be fine. Just as long as the Voc doesn't rise too high if it gets cold where you are.

0 Likes 0 ·