midmaik asked

Extra Grid Meter for PV Inverter output measurement?

Hello,

I have following components

  • Victron Multiplus
  • ET112
  • Cerbo GC
  • 5 EVT300 with Solar Panels
  • 3 pylontech batteries

the ET112 is installed on the AC Input side of the multiplus, my AC Loads are connected on the AC Output 1 side, on that there are also the 5 EVT300 with Solar panelsunbenanntx.gif

Is it possible to addPV Inverter Power widget in that graphic ?

Or do I need a second grid meter ? Or do I need to installe the ET112 on the AC Output side ?


Thanks

Maik

AC PV Coupling
unbenanntx.gif (71.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

you need a AC Sensor the main active output (total output from the EVT300) from the grid tie goes through this and thus it sensors the output power and then connect this unit to the Aux 1 or Aux2 and install a ac Current sensor assistant in the inverter and the tile will then show.


You can also use another ET112 as well so you have two otions