Multiplus II showing negative values while charging on the GX

Hello,

I have a setup consisting in one battery bank (lithium 3rd party), 2 SmartSolar MPPT´s, 1 Cerbo GX and 2 Multiplus II 5000.

After playing around with the configuration of these multiplus inverters, by configuring them in parallel, split phase or operating as standalone devices (in this case running only one device at a time), I come to a point where one of the multiplus works perfectly fine (in all the configurations above) and the other is behaving very strangely.

Basically the odd multiplus, while charging, presents the charging amout one the Cerbo GX, as a negative load on the ACout, instead of presenting it as a positive load on the ACin.

If checked the wiring, and the shore power is connected to the ACin.

MultiPlus Quattro Inverter Chargercerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
eliott avatar image
eliott answered ·

Hi! we had the same issue, a firmware updated solved it. it works for us with 82.