My inverter keeps restarting every 20mins or so, shows low battery solid light then goes back to inverting after like 5 -10 seconds.
I have lead-acid batteries connected to the Multiplus 24/3000
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
My inverter keeps restarting every 20mins or so, shows low battery solid light then goes back to inverting after like 5 -10 seconds.
I have lead-acid batteries connected to the Multiplus 24/3000
Then I would measure the battery voltage at the battery and also at the inverter. There are also setting inside the inverter for low battery warning and low battery shutoff and voltage to turn back on. check these with a MK3 VE-BUS to USB unit
Suspect the unit is shutting off on low battery off (about 20v) and then coming back on when the LA batteries slowly recover (24 volts) from the load applied and it then turns back on.
If the setting have not been changed from default then I suspect the batteries are Flat or cant supply the power required anymore and may need replacing.
Check your voltages and monitor them until it turns off Really the voltages should NOT go under 24.4 volts and preferably 24.8 volts