Good day,
I've got the following system:
3 x 10KVA Quattro's
CCGX
30kWh Lithium battery (freedomWon)
25KVA FAW (charging limit of 4kW per phase to preserve the generator at approx. 50% running mode) Generator comes on at 20% SOC automatically, stops at 75%
10kWp PV (with 2 x 250/100 Mppt's)
It seems that the Quattro disconnects the generator as soon as the load draws more than 4kW on any phase when the generator is running, then tries to connect again. It will only connect when the load is reduced.
Is there a way to set the victron system that it maintains a constant charge by default (currently set at 4kW per phase), but allows more power from the generator when required for the load occasionally?
Hope it makes sense?
One solution I thought of is to put each geyser (1 per phase) on contactors disconnecting automatically when the generator comes on