Hello, I have a multiplus II with RPi 3 like gx
device, I have a problem with the meter et112, some times it appeared like disconnected, I reviewed the wires and they are ok. Any idea? Thanks in advance.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello, I have a multiplus II with RPi 3 like gx
device, I have a problem with the meter et112, some times it appeared like disconnected, I reviewed the wires and they are ok. Any idea? Thanks in advance.
Hi Palom 170. Is it using the Victron USB connector ? The problem I encountered is related to RFI created by the inverter, if the cable is too near of it. By moving it 5cm, it did resolve the issue, you should give it a try.
Michel