question

perseverance avatar image
perseverance asked

MPPT 100/50 Controller not connecting

I have a solar charging system with 2 banks: 4 panels on the roof and 2 on a wing at the stern. They connect to 2 x MPPT 100/50 controllers charging 3 x 200Ah Lithium batteries for house supply.

This morning the controller for the roof panel reads "connecting" and I have not been able to rectify this. On visual inspection nothing has changed, all connections look good. The installation is only a few months old. Powered everything down at breakers and restarted but no joy. Found no reference to this error message in the manual.

The bulk light is on and flashes once every 10seconds or more. The wifi connection to the roof panels shows normal operation.

Hoping someone can help or send a link to steps to fix. TIA


img-20210421-092038.jpg

129.jpeg

MPPT SmartSolar
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

Swap the displays to see if the problem remains at the same charger or moves to the other charger (then the issue is that display or cable).

0 Likes 0 ·
1 Answer
Eduard avatar image
Eduard answered ·

Suggest that you first check the software and update.

Latest is 1.56.

2 |3000