New Li Battery Catamaran Install keeps shutting down

We recently replaced our AGM house batteries with 5 Smart Lithium 12V/200AH (V 1.20) or 1000AH. Added Smart BMS CL 12/100 (V1.06), SBP 12V/220A (V2.08, Bootloader V1.02), SmartShunt 1000A/50mv (V4.05), Cerbo GX (v 2.63)and have a Multiplus Compact 12/2000/80 (V unknown).

1. While sailing and using the electric winch the system reboots. Both motors on.

2. While sailing, motors on, the system rebooted Nav system, autopilot, VHF (12V electrical)

3. Sailing w/o motors -12v electrical quit. Had to restart our engines to restart the 12V system.

4. At the dock we started the generator and we lost the 12V electrical system. The 110/220V system works fine. At this point the 12V system has not returned.

We are working with our Victron Installer and local Victron Rep for the past month as items 1-3 have recurred but the solution has not been found. Any thoughts?

MJ

screen-shot-2021-04-18-at-111743-am.png

Not shown is the Port side Start and Generator battery which are connected to the starboard side via a Samlex 160 Battery Separator


MultiPlus Quattro Inverter ChargerLithium Batteryinstallation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nebulight avatar image
nebulight answered ·

have you checked the status of the smart battery protect when the 12v cuts out? the app should show if the system was disabled by remote. Can you also take a screen shot of the battery protect screen from Victron Connect? Curious to see what Mode you have set. It should be C with the way your install is setup.