question

apple047 avatar image
apple047 asked

PV meter on the output of inverter data

Hello,

I have an ESS running with Cerbo GX, Multiplus II, and an AC coupled inverter on the output of the multi. Until recently i didn't monitor PV production but today i installed an EM111 meter, it's communicating fine however I cant configure it that its connected on the output of the multi. I select the position of the meter "AC Output" but its reverting back to "AC Input 1" once the page refreshes.

This causes "AC Loads" calculations to be incorrect.

I did set up in ESS assistant the PV inverter on the output and by the looks of it the generation is being counted twice.

Thanks in advance for assistance

George

1618670922835.png1618670899892.png

ESSEnergy MeterAC PV Coupling
1618670820889.png (115.7 KiB)
1618670899892.png (103.1 KiB)
1618670922835.png (129.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
apple047 avatar image
apple047 answered ·

After a bit of reading it looks like i have the same problem as Thomas

https://community.victronenergy.com/questions/85166/consumption-is-showing-proportional-to-pv-inverter.html

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wilga avatar image
wilga answered ·

Same problem here (Venus OS v2.90).

Solution: setting the meter position to "AC Output" must be done under settings > meters to make the system correctly accept the change.

zwischenablage01.png

zwischenablage02.png

zwischenablage03.png



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.