Is it OK to simply change the default SOC bulk parameter setting (85%) in VEConfigure3 to a higher value, say 95% or even higher?

BMV Battery MonitorVEConfigure 3
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Probably not. A lead battery is typically around 85% full by the time the system switches from bulk to absorption.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Elimac avatar image
Elimac answered ·

Allow me to ask here another question that might also be relevant... 85% or 95% of what capacity? In the same menu in VE configure where this is set, the battery capacity should be the C10, C100 or other value? If incorrectly filled, this will have also the same effect in wrong SOC values...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

neoneddy avatar image
neoneddy answered ·

You can but you'll risk boiling off your electrolytes.

2 |3000