Multiplus 2 - 3 phases - ESS mode 3

Installation with 3 Multiplus 2 + BYD batteries - Venus GX - ESS mode 3

Our controller is communicating with Venus GX by Modbus TCP.

When sending a modbus command on slave id 242 , register 37, we control A phase of the system correctly.

Therefore, when sending a modbus command on slave id 242 , registers 40 and 41, we get the error " GatewayPathUnavailable"

How should we control B and C phases ?


ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
bbmz avatar image
bbmz answered ·

I hope you found help somewhere else (since it‘s nearly two years later). But some advise for other users:

Keep in mind, that you have to configure your inverter / VE-Bus setup first to a 3-phase system and you have to configure a ESS-assistant on each inverter afterwards.


Your description sounds like you only configured the 3-phase arrangement (on all 3 devices) but missed to configure the ESS on the L2 and L3 devices.