Hello Victron community,
We are using Quattro 48/15000/200-100/100 with CCGX and our own battery and BMS. We are going to connect the system to a charging site which includes 3 single phase chargers and currently each of them is limited to 3.6kW each.
With the system installation, the chargers would be able to go up to 7kW each, by providing ~10kW of battery power out of 20kWh battery bank.
We are using our own control loops which means we operate the system on ESS mode 3 and managed to communicate and control the inverter pretty well.
However, when tested the inverter in the lab with a simple heater of 600W as load and smaller battery pack of 2kWh, it seems that it couldn't handle this peak and move itself to passthru mode...
When we went back to the manual we noticed that there is a constrain of 400W/s ramp up time. However, in our site we don't have a precise control on the ramping time of each charger on site.
Need some help to understand how should I manage it?
- Is the inverter limited to work just with a loads that can be managed to 400W/s?
- Is that relevant for ESS mode 3 only? Can I operate it in other mode and avoid this restriction?
Would appreciate any suggestion or assistance on that
Let me know if any further information is required.
Thanks in advance