Hi,
I am reaching out because I really need help configuring the Victron SmartSolar 150/35 and the SmartShunt 500A for my 48V AGM-battery (8 x Fullriver DC400-6).
Since I live in Norway and charging is very limited in the period from November - February this is tricky!
I have a potential for (theoretical) 33,6A solar charge with my six 325W panels (3s2p), but in the mentioned period I rarely see much current (aprox. 4-6A). So if I follow recommendations with 3-4% of C20 (415Ah) for my batteries I will have a problem with SOC calculations in the shunt. As I have understood the shunt will estimate a 100% SOC when 3 conditions are met: Charged voltage, tail current and charged detection time.
In my case the voltage for charging will be high enough to achieve "charged voltage" every day (because of my 6 panels), but the current will in periods be as low or even lower than the tail current setting if 3-4% (C20) is used. I'm afraid this will result in a very inaccurate SOC calculation..
For the Smartshunt I need help configuring the following settings:
- Charged voltage? Here I have seen that 0,8V below float is recommended, while others recommend 0,8V below absorption for Solar - what is correct?
- Discharge floor? For AGM I believe this value should be no lower than 50% based on what I have read - correct?
- Tail current? In my head I would have to set tail to 0,8% - 1% or even lower and adjust this to about 2% or slightly higher as charging gets better from mid February - sounds resonable?
- Charged detection time? For the charged detection time I have read that 8-10 min would give a better calculation than the default 3 min for solar charging with low current - correct?
- Peukert exponent? Here I have no idea what to configure, all my reading suggests different options so please help me.
- Charge efficiency factor? The only thing that is certain is that the standard 95% must be way too high for my system, and maybe 70-80% would be more correct?
- Current threshold? I have no clue what this means and need help
- Time-to-go averaging period? I have no clue what this means and need help
For the Smartsolar I need help with these settings:
- Temperature compensation? my batteries says -4mV per cell, and eight
6V batteries in series would then be -96mV according to my calculations - correct?
- Re-bulk voltage offset? Here I have no idea what to set and need help
- Maximum absorption time? My batteries should not be in absorption for
more than 8 hours, so maybe the default 6 hours is ok?
- Tail current? Here again I have no idea what to set because of the
varying charging conditions. My Fullriver batteries only have info of
the state when absorption changes to float: I = 0.012 - 0.02 x C20.
If I understand this correct the tail current will taper down from 8,3A
(0,02x415) to 4,98A (0,012x415). My main concern for this is that I
rarely see 8A charging in the darkest period of the year.. The default
value set on the SmartSolar is 1,0A, will it be OK to leave it at
default and max the absorption out to the battery max rating at 8 hours?
I will let the SmartSolar use "Adaptive mode" for Absorption.
I am really sorry to bother you guys with all my questions, but I know the knowledge is in this community and I haven't been able to get any reasonable answers from the "experts".
I would highly appreciate it if anyone could help me.
Thanks in advance!