I have a 24/3000/70 Inverter/Charger. My battery bank is consisting of 9 SPRE 12 225 Trojan batteries that are connected in three strings of 24-Volts. The battery maximum charging current specified by the battery manufacturer is 13% of C24, which is a little more than 26 amps for my batteries. My question is, considering the three parallel strings, can I/should I set the charging current up to three times the prescribed charging current if the inverter or the size of the input wires and upstream devices support it. I am aware that this inverter is rated for 70 amp.
The next question is, how do I manually put the device into equalization mode? And what would be the consequences of the setting discussed above over this procedure?
Thanks in advance.