question

Matthew Walsh avatar image
Matthew Walsh asked

Consumption on non-backup phases under critical loads

Hi,


I have a system installed as per below:

fra001-system-layout.png


The issue that is occuring is that the AC loads in L2 / L3 are showing up in the critical load display and my PV inverter shows as just one figure where it used to show per phase. This occurs during the day when there is PV being generated.


At night time, it appears to display correctly as per the below screenshots:

1617127373553.png


1617127381489.png


My ess settings are as follows for the site:

1617127580897.png


And my energy meter settings are

1617127568393.png

1617127553670.png


I would like to know if it possible to correct this with the current setup on site?



ESSEnergy Meter
1617127373553.png (133.8 KiB)
1617127381489.png (131.1 KiB)
1617127446729.png (42.3 KiB)
1617127514758.png (28.6 KiB)
1617127518452.png (28.6 KiB)
1617127553670.png (17.5 KiB)
1617127568393.png (15.0 KiB)
1617127580897.png (29.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Warwick Bruce Chapman avatar image
Warwick Bruce Chapman answered ·

You’re telling the system your three phase PV meter is on the output (critical loads) of the Quattro - but it is a single phase system.

If you moved the PV inverter on the red phase onto the input side and changed the position of the PV meter accordingly, I think the issue would go away.

I assume what you need to keep the current architecture is to be able to specify:

1. the position of grid meter relative to Quattro on that phase; but

2. then also specify a different position for the remaining phases, right?


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthew Walsh avatar image Matthew Walsh commented ·

Yes, but if we move the PV Inverter to the input we lose the solar in an off-grid state.

Ideally we would like to as you have stated in the settings specify those two points so that there is more flexibility and also correctly displayed and recorded data.

0 Likes 0 ·