barnbiketom asked

150/60 wont hold presets AND code 38 appeared

4 100w panels in series 90v open circuit @ 5.4 A. 70' run with 10 ga wire to a smartsolar 150/60. One AmpereTime 100ah lifepo4

I cant seem to get it to remember any presets. If i put it on lifepo4. Then reconnect to the app.. it is on User defined...??

Additionally, the first time i ran the system, i got a code 38..

History shows 15+ volts.

Why


screenshot-20210321-083257.png

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Barnbiketom

Most likely your battery bms shut off.

https://www.victronenergy.com/live/mppt-error-codes#err_38_err_39_-_pv_input_shutdown

The article explains how to recover from the error.

You may need to set your charge current down (what does the battery recommend) or lower your charged voltage slightly as the battery bms possibly shitdown from a slight overvoltage.