Solar feed to AC Out-1 + AC Out-2 on a Quattro ?

Hey! Please advise, it is possible:

  • We have a stable input 230V 100A (sometimes there are blackouts)
  • We want to supply Quattro 48/10000 and connect PV ≤9kW via controller MPPT 250*100 *2 pcs
  • The battery will always be charged.
  • Maximum load on AC output-1 ≤ 7kW
  • Maximum load on AC output-2 ≤ 10kW (when the input network is available)

Q1: Will solar energy be shared between AC Out #1 and AC Out #2?

Q2: If the consumption is small during large PV generation, is it possible to set up a power discharge to the grid?

Q3: Do I understand correctly that when AC Input #1 disappears, AC Out #2 will automatically turn off?

Thank!

1234455555555.jpg


MultiPlus Quattro Inverter ChargerESSgridsolar
1234455555555.jpg (332.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Warwick Bruce Chapman avatar image
Warwick Bruce Chapman answered ·

Note, I assume 9kW of PV and not 9000kW.


Q1. Yes.

Q2. Yes, enable "Feed in excess DC" in the ESS menu

Q3. Yes, that is the default behaviour.