Input current limit being exceeded - Multiplus

Hi,


I have a 48/5000 Multiplus 2 with a BT Smart dongle.


I have set the Max Input Current Limit to 10a via the BT dongle but when I plug the gen set in to top up the batteries it charges at Maximum current which exceeds the generators 3,700w running capacity.


dbe72bf7-b8a9-4dec-85df-05ab0efd13ed.png

Multiplus-IIinput currentVE.Direct Bluetooth Smart Dongle
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

Your AC in is not connected.

Your battery is not being charged.

AC out is 189w.

HMmm.

0 Likes 0 ·
88benjy88 avatar image 88benjy88 klim8skeptic ♦ commented ·

It is connected, the inverter doesn’t have time to evaluate the input current etc before the gen set overloads. The BT dongle interface shows this before the gen set cuts out. If the gen set would hold out another 15 seconds or so I believe the UI would show more details

0 Likes 0 ·
1 Answer
seb71 avatar image
seb71 answered ·

What if you limit the battery charging current (in Multiplus)?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

88benjy88 avatar image 88benjy88 commented ·

That’s the next step but I have to use Ve Configure for that. So another $100 accessory from Victron. I ordered one today.