Hi,
Can anyone tell me the reason that victron state not to connect the midpoints in a 2s2p Bank (to make 2p2s)?
Im having trouble getting my bank in balance, and i think temporarily connecting the midpoints for a cycle or two would help to bring them in line with each other.
Any feedback greatly appreciated =)
*edit - of course i would fuse this connection, rather blow a small fuse than have fireworks!




I appreciate your reply. I will disconnect the midpoint as I wait for the "Battery Balancer" to arrive. When I read Victron's blog re the balancer, they were describing the problem I am having. I have returned to 28.4 absorption, 27.0 float, 99% efficiency, 1.01 Peukert, but 15 minutes absorption, on my SmartSolar and SmartShunt. I will expand that to default 2hrs. My Multiplus is returned to same but I saw no place for Peukert's on VE.CONFIG. I will look again and return to longer absorption there too. I should have the balancer by Wednesday. Allegedly, the balancer will solve the problem.
The balancer has only reduced the problem. I am still ramping to 2.80% divergence on the tail of absorption. Within minutes of switching to float, the divergence is under 0.5%. HRx