Quattro 10k - AC- IN - 1 Won’t accept Grid Power?

2 -Quattro - 10k inverters not accepting grid. Will start to load then disconnect.

60hz

120 v

Doesn’t drop or spike just disconnect.

Any help would be appreciated.

MultiPlus Quattro Inverter Chargergrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

check to see if you are getting voltage sag as when they connect they would be charging the battery and thus drawing quite a bit of current and this maybe causing the incoming line voltage to sag down to the disconnect voltage. Try reducing you max charge rate and see if that stops the line voltage sage if thats occurring