Fuse size recommendation

Going off grid!

I'm designing my off grid system and trying to figure out the correct fuse size for my inverter to battery. Using two 48/10000/140-100/100 120V split phase configuration, 48V (50KW) Li batteries, 100A 120 /240V main panel at the house

any help or suggestion is appreciated

solar sizing
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
seb71 avatar image
seb71 answered ·

Fuses are chosen to protect the wires.

You should find in the inverter manual the recommended wire size (cross section) for inverter-battery wires and recommended fuse value for this wire.