UK Grid ALoMCP - G59

Updates to the G59 standard require confirmation that ROCOF and VS are not used as a means of protection.

If they are they need disabling. Or may need the settings amending.

(useful brief overview from Comap - https://www.comap-control.co.uk/g59-3-4-accelerated-loss-of-mains-change-programme/)

The ENA has a database collating the responses from Manufacturers - and what course of action may or may not be required.

Do any Victron devices use ROCOF or VS loss of mains ?

Thanks

Chris

ESSgrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nigelv avatar image
nigelv answered ·

Hi Chris

G59 is obsolete now in the UK, the full method Hz and timings for loss of Mains are listed in the G98/99 certificate on our web site product page

Email me if you need details on these, I can send you the full document nvincent@victronwnergy.com