Can Multiplus share ground and neutral of 50 amp service with leg that goes straight to panel

I’d like to be able to utilize 100 amps of power (50 on each leg) when plugged into 50 amp service. 1 leg will feed through multiplus and power half the panel. The other leg will feed directly to other half of panel. Can I simply splice off of neutral and ground coming into RV from 50 amp service and route 1 neutral/ground pair to multiplus with line 1, and the other neutral/ground pair to panel with line 2? Thanks!

Multiplus-IIMultiPlus Quattro Inverter Chargermultiple inverters
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

caza-gomis avatar image caza-gomis commented ·

@Guy Stewart (Victron Community Manager) could you please advise?

0 Likes 0 ·
1 Answer
wkirby avatar image
wkirby answered ·

In theory this should work.
It is however difficult to answer here because it really depends upon the local wiring rules for your region. Your question is more related to the panel wiring and making sure that it meets code rules. It would be better to direct this kind of question towards your local electrician.