Quattroi Overload

I have a Quattro 48/10000/140 which frequently overloads when supplied from AC2. It never overloads when supplied from a genset via AC1. The only load is a fluorescent light. With the load disconnected and the Quattro in Charge Only mode, the overloading problem still occurs.

AC2 is supplied with 240V AC from an Emerson Unidrive invertor. I do not know any details for the voltage waveform that is connected to AC2. It registers 0V on a digital voltmeter, but shows 240V on an analogue meter. Any suggetsions for a remedy would be much appreciated.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Henk avatar image
Henk answered ·

I would suggest the enerdrive is not a power supply inverter.

VSD, Variable Frequency Drives for motors cannot be used.