Every time I allow each inverter to attach independently to power source I loose the assistant and every time I add the assistant the inverters lock together again?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Every time I allow each inverter to attach independently to power source I loose the assistant and every time I add the assistant the inverters lock together again?
More information on your setup is needed , but basically both inverters have to always be connected and both have to be on as they are always talking to each other. to adjust the in power on one and not the other adjust that POWER assist setting by using VE config on opne unit to 30 amps and the other unit say 1 amp, this may work. OR you could try ignore AC IN 1 on one inverter and not the other, there are two assistants to setup for that General flag and programmable relay.
I how this maybe of some assistance with your question.
Parallel, split- and three phase VE.Bus systems manual
Theory on wiring large systems PDF
Three-phase and parallel system theory training presentation
Three-phase & Parallel installation training video
MultiPlus Product page / Quattro Product page
MultiPlus 230V Manual / Quattro 230V Manual