I'm trying to set up ESS in VE Configure 3 and it requires me to choose a grid code. I'm in South Africa and when I choose it from the menu, it gives the following error "this device is not equipped with internal interface protection"
I'm using a Quattro 48V/10000VA/140A model with a firmware updated to 2653433
If you look at the following link https://www.victronenergy.com/live/ve.bus:grid-codes-and-loss-of-mains-detection#veconfiguregrid_codes_loss_of_mains_detection you will see an image in section 3 where South Africa had been selected.
So did I get the wrong device or what am I doing wrong? Or do I need external LOM devices?
When I run VE Configure 3 and choose "Fake target with full options" then I'm able to select South Africa in the simulation without error codes
I don't want to feed back to the grid, however ESS setup forces me to choose a grid code