Multiplus shuts down without any apparent reason

Why would the Multi in an EasySolar-II 48/3000 GX out of the blue shut down and automatically restart an hour later with no apparent reason? No alarm logged, no notification, AC load at time of shutdown below 100w, battery full, grid good (virtual switch set to "ignore AC input")?

Multiplus-II
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·

Hi Nama, there are lots of reason this could happen but we need to find out in your case is why.

Hopefiully you have a GX unit and have a connection to the vrm, look at all your graphs at the time of the shutdown and see if you can see a reason, also download the excel data file and again look at the time and the reasons reported.

If not then you will need to see what the battery voltage is when its shutting down, this will be the main reason I would think, and it then comes back on when the solar has charged the battery back to its restart level.



0 Likes 0 ·
nama avatar image nama Paul B commented ·

Thanks Paul, on-board GX in EasySolar. Nothing unusual on VRM, hence this question on the forum. AC Output 58w at time of shut down (security system and a few lights), AC within normal parameters (Volts and frequency) and battery 53.09V with SOC 98%. Happened around 22h30, so no PV power present at the time.

0 Likes 0 ·
Paul B avatar image Paul B nama commented ·

Guys comment is quite valid and a real possibility that a cell has gone hi, these are really hard to see as well, so have a look at the bms history in the battery if it has one

0 Likes 0 ·
3 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Nama,

I presume that this system is using a lithium battery. The most likely cause is something that upset the battery BMS, and it shut down to protect itself.

This can sometimes come with a warning or alarm, but not always.

It could have been a cell imbalance, and this is the most likely cause if the battery was near 100% fully charged. But it's tricky to say for sure without having access to the more detailed internal monitoring (maximum / minimum cell voltages).

If it has just been a once off event, probably best to just wait and see if it occurs again before digging too much further.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nama avatar image
nama answered ·

Thank you Guy. It is a lithium battery yes, a Freedom Won. This is in fact the 2nd occurrence (identical circumstances)... previous instance about 2 months ago. I'll take it up with the FW team as I really need to get it resolved due to the fact that this system power a sensitive security system that cannot afford any downtime.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Another troubleshooting step that is a good idea to help exclude from the possibilities.

Step 1. Check for the latest firmware with all the manufacturers (batteries, chargers, inverters and control units, etc).

Step 2. Remove all communications cables and replace them with new, factory made cables. Make sure there is at least 10cm distance between any communications and power cables (where all possible).

0 Likes 0 ·
ako avatar image
ako answered ·

I ha exactly the same issue earlier in the week , everything completely normal but the Multiplus shut down for 28 minute . VRM only shows a gap on each of the widgets because the Internet router will have gone off also . The log file which was recording every 1 minute has 28 mins missing also . Not only can i see no reason for it turning off i cant see any reason for it booting up again . Absolutely everything was well within limits before during and after .