Help with melting terminal mppt

20201115-145101.jpgMPPT100/30 melting PV pos terminal. Recently occurring after moving controller20201115-145109.jpg

Help
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
ceriw avatar image
ceriw answered ·

that would suggest that the screw was not torqued to the required spec after the system was moved, and arcing has occurred, melting the connector.