I have an EasySolar-II GX in ESS mode, connected to the grid, but with feed in disabled and the grid setpoint set high enough to ensure no inadvertent feed in. Let's call this system the house system.
I'm considering adding more PV capacity in an outbuilding (in other words, this would be a mainly separate system, with another EasySolar or Multiplus, it's own separate MPPT controller, and separate batteries). Let's call this system the outbuilding system. I would be thinking of also running this system in ESS mode.
This downstream system (outbuilding) would get it's AC IN from the one I already have (house system), so if PV or battery in the outbuilding weren't sufficient to supply it's loads it would pull power from AC IN to supplement (up to the AC IN limit) and so would be pulling that additional power from either the house PV, house batteries, or possibly at times the grid via the house system, so far so good.
But if the outbuilding system has surplus power (it has for example good sun, fully charged batteries, and light loads in the outbuilding), can I now feed power back into the house?
I'm thinking that from the point of view of the outbuilding system this would basically be doing grid feed in. It has no idea where it's AC IN is coming from, so if it is set to export AC and DC surplus to the grid, it will just sent that power up the AC IN wires to the house, where they will meet the AC OUT of the house MultiPlus/EasySolar/Whatever.
From the point of view of the house system, it will be like using a PV inverter (https://www.victronenergy.com/live/ac_coupling:start), in that it's receiving power on both AC IN (grid) and AC OUT (downstream Multi/EasySolar).
So during a period of heavier load in the house, the downstream solar system should combine with the house EasySolar to power the loads.
During a period of lighter load in the house, suplus power coming in on the house EasySolars AC IN (from the outbuilding) would go backwards through the inverter charging the house batteries, is this correct?
What about "Frequency Shifting" as described on the page I linked to above. That page describes this as being the method used by the multiplus/easysolar to control the output from the PV inverter so as to prevent it outputting excess power that has nowhere to go (say the house load is zero, house batteries are 100% charged, house does not feed in to the actual grid). Does this same principle apply if the downstream system was not a "PV Inverter" but instead was another EasySolar or MultiPlus as I'm describing?