SmartSolar MPPT 75/15 turns load off and on twice a day

I have about a 1-amp load connected to the load terminals of a SmartSolar MPPT 75/15. Twice a day (at about 6:30 and 17:25) the power to the load terminals if turned off and back on. The times vary by +/-10 minutes. Prior to the end of daylight-saving-time the incidents occurred at about 7:30 and 18:25. I can see this in the logs of two of the attached devices that report power lost/restored incidents. There is no event in the attached load that occurs at those times. Any ideas as to what is happening?

MPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @RJKEPPLE,

There was a bug recently introduced, but now fixed. Please update VictronConnect, and then the firmware on your MPPT.

That should resolve it.

A bit more info here - https://www.victronenergy.com/live/victronconnect:beta#v535_released_officially