question

Matt Knight avatar image
Matt Knight asked

Grounding MPPT 100/50

We are soon to be installing a Victron SmartSolar 100/50 in our RV. It will be connected to 4x 100W solar panels in a 2s2p configuration. Our travel trailer’s 12V ground is connected to the trailer chassis.

Do I need to connect the solar panel negative to the PV- on the Victron solar charger or can I instead connect PV- to the existing common ground (ie the chassis) and connect the solar panel negative to the common ground too?

This is how another MPPT Charger we have installed is wired but I see no mention of it in the Victron documentation. Doing this would simplify our cable runs.

solarwiringGrounding
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

You should connect the solar panel negative to the solar panel negative terminal on the MPPT. Do not use your grounded vehicle chassis to connect the negative of the PV string.

I understand this will mean an additional cable run.

From the Wiring Unlimited Draft :

Do not ground the positive or negative of the PV array: the PV negative input of the MPPT is not isolated from the negative output. Grounding the PV will therefore result in ground currents
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matt Knight avatar image Matt Knight commented ·

Understood - thank you! This is the information I was looking for.

0 Likes 0 ·
vivuscraig avatar image vivuscraig commented ·

@Guy Stewart (Victron Energy Staff) Guy, can I ground from the controller directly to the chassis? From what I understand, the negative of the PV string should go directly to the controller. Also, the negative of the battery should go directly to the controller. So can I run the ground from the ground screw on the side of the controller to the chassis.


I think that is what you are saying.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ vivuscraig commented ·

Yes, you can connect the ground screw on the external case of the controller to the vehicle chassis.

0 Likes 0 ·
Matt Knight avatar image
Matt Knight answered ·

@Guy Stewart (Victron Energy Staff) just following up, is a circuit breaker required on the positive output (battery) side of the charge controller? I assumed one was but I just noticed the specs show it contains “Output short circuit” protection. I will be including a breaker on the positive input (PV) side.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Best practice is to have a circuit breaker or fuse sized 75% below the current rating for every piece of wire.

In the case of the positive output on the battery side, a slow blow High Rupture Current fuse is appropriate, and should last the life of the installation.

1 Like 1 ·
Matt Knight avatar image Matt Knight Guy Stewart (Victron Community Manager) ♦♦ commented ·

That was my design but then I read that the charger has built in protection. I wondered if that were sufficient but it sounds like not.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ Matt Knight commented ·

There is some protection inside the units, but it isn't rated to the wire you connect. It is also not user replaceable, so you are FAR better off with a serviceable fuse.


1 Like 1 ·