question

Stijn Dhondt avatar image
Stijn Dhondt asked

Sheduled battery charging based current grid usage

Hi,

I was wondering if there already is some posebility to charge my battery without going over 2,5Kwh on grid usage.

This limit will be on our head soon even on night usage so i would try to stay bellow the 2,5Kwh limit even when charging the battery combined with the current grid usage.

battery charginggridcharge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Stijn Dhondt

It is possible to do so. Set your input current limit down to the desired level.

You can also set your charge tab up within lower amps for charging the battery.

https://docs.victronenergy.com/veconfigure.html#charger-settings

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

CristiMV avatar image
CristiMV answered ·

The easiest way is to do it via DVCC...dvcc.png