Does the above inverter/charger have a bonded neutral / ground ? I'm using a EMS that needs a bonded neutral
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Does the above inverter/charger have a bonded neutral / ground ? I'm using a EMS that needs a bonded neutral
Hi @ragscar, welcome to the Community!
Neutral/Ground may only ever be bonded in one place, so while the unit is plugged in to "shore power", the neutral/ground bond is provided from shore.
While inverting, the N/G bond is provided by the unit itself, so long as the ground relay is not disabled (see Section 10.3.2 of the VictronConnect VE.Bus Configuration Guide).