Are these two multiplus compatible for Parrallel

Hello,


I have 2 multiplus II with the same PN (PMP482305010)

But the SN are different :

- HQ1918*****

- HQ2016*****


When I look on the this forum I understand first that HW is defined by SN, but now it look they cannot accept the same firmware because of SN starting with diferent digit (19 vs 20) https://www.victronenergy.nl/upload/documents/manual-VE.Bus-firmware-versions-explained-EN.pdf

Are these 2 multiplus not compatible for using in parallel on a single phase?


Note: I just buy these 2 multiplus... I did not think it could be an issue on compatibility.


Thank you in advance for your answer/help.


regards,


Arnaud B.


[moderator's note: edited to remove last 5 of device SNs]

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Meine_Energiewende avatar image
Meine_Energiewende answered ·

In my opinon this will work as the part numbers are the most important part of a parallel or 3 phase setup. I have a 3 phase setup and the SN are different too but it works quite nice. I also think your inverters will accept the same firmware version.

Hope it helps

Jens

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

arnaud-b avatar image arnaud-b commented ·

Thank you stxshadow.


I was scared by looking more pessimistic answer based on SN: https://community.victronenergy.com/questions/18300/increasing-old-multiplus-5000-setup-to-10000-va-pa.html

When some other discussion only mention to have the same PN.

Note: HW rev are 09 and 14 on my two multiplus.


I will try to upgrade them... but I didnt see how to "force" the same firmware as we should update them separatly.

0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The SN is always different, each device has it's own unique SN.

Important is the part number and that both have the same firmware.

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems