question

john2019 avatar image
john2019 asked

Can I mount the Victron Lynx DC Power-in upside down?

Hi, All

Just a quick question, as room constraint. Can I mount victron DC power in and DC Distributor up-side -down. Which is cable holes up rather through bottom.

Thanks

victron productswiring diagram
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Yes, it is often done like this.

A downside is the writing is upside down, also it could catch dust or moisture, so it's best to have some kind of cover. You can see an example in this recent case study.