Ve bus error 1 cause system shutdown or not

If one inverter of 15 *10 k three phase system shutdown and error 1 appear. Is it cause shutting down for all system or not?

offgridVE.Bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Abdallah Salamah

https://www.victronenergy.com/live/ve.bus:ve.bus_error_codes#error_1_-_device_is_switched_off_because_one_of_the_other_phases_in_the_system_has_switched_off

The system will be switching off because one of the devices has an issue. See the article above for reference.

Trouble shooting: Look for the failing phase, which will be the phase that is not showing VE.Bus Error Code 1. And check the LEDs on that phase to find out what the reason was for the shut down.