Fault level for Quattro 10kVa inverter

Hi, All

I post the question again, Anyone knows the fault level for Quattro 10kVa inverter. This is for standalone system installation to replace grid in Australia. Utility wants to make sure inverter is able to deliver sufficient amount of fault current to trip their 16A circuit breaker in 400ms.

Many thanks


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@John2019

All the certificates of compliance are available

https://www.victronenergy.com/inverters-chargers/quattro#certificates

The full rated transfer capability of a 10kva is 140A excluding it's overload capabilites.