I have a EasySolar-II GX and when I look at the battery current in the connect app it is about twice the value in VRM "System - Battery Voltage and Current". Is this a bug or do I missunderstand something?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi!
I have a EasySolar-II GX and when I look at the battery current in the connect app it is about twice the value in VRM "System - Battery Voltage and Current". Is this a bug or do I missunderstand something?
In your screenshot you are looking at the current that the MPPT charger is generating. Not all of this current will go to the battery, some of it will go to loads. Load would include the quiescent running of the inverter and the GX. Subtract the current going to the loads and then you are left with the actual battery current which is shown in VRM.
Thank you for your answer!
That makes me think about which value (mppt or acutal battery current) that is used to end absorption phase due to reaching the tail-current configured in the mppt/connect app ?
If the mppt value is used, which I think is the case, the absorption phase would be too long and risk battery to be overcharge. What am I missing here?